I am using ESP_Easy_mega_20210114_normal_ESP32_4M316k on a ESP32.
in the following rule I start the event "ControlSZ=0".
It pulses two GPIOs with LongPulse for 28 seconds.
In parallel I start a timer (already with TimerSet_ms as the difference without _ms was bigger), set a variable to 28 and let the timer decrease every second 1 from the VAR#20.
the outcome is that the Pulse of the GPIOs ends and the counter is running nearly 3 seconds longer.
below also the complete log, following timestamps:
181338027 trigger the event
181339290 Pulse first GPIO
181339295 Pulse second GPIO
181339305 Start timer_ms (VAR#20 already set to 28 before)
181340307 enter the timer-part in rules
181340353 reset the timer to 1000msec (already on most top in the event rule)
181341762 enter the timer-part in rules
181341808 reset the timer to 1000msec
a parallel running Rules#Timer=8,1 which is set to 28 Seconds is running out in time and overtakes the periodically reset timer by over 3 seconds:
181339031: ACT : TimerSet,8,28+2
181367032: EVENT: Rules#Timer=8,1
Difference: 28001 (oh, it looks like the addition there does not work - have to rework this)
I have NOT checked SendToHTTP wait for ack
I know, jitter may influence things - but can I do something against it - or to make it more exactly?
Or, as the GPIOPulse is working exactly, is there a way to read in rules the seconds passed from the pulse?
Any ideas?
Best regards
Alois
I compared and calculated the differences between the timestamps:
Timestamp Diff
181339305 ACT TimerSet_ms,7,1000
181340307 1002 EVENT Rules#Timer=7,1
181340353 46 ACT TimerSet_ms,7,1000
181341762 1409 EVENT Rules#Timer=7,1
181341808 46 ACT TimerSet_ms,7,1000
181342811 1003 EVENT Rules#Timer=7,1
181342857 46 ACT TimerSet_ms,7,1000
181343992 1135 EVENT Rules#Timer=7,1
181344037 45 ACT TimerSet_ms,7,1000
181345040 1003 EVENT Rules#Timer=7,1
181345085 45 ACT TimerSet_ms,7,1000
181346087 1002 EVENT Rules#Timer=7,1
181346131 44 ACT TimerSet_ms,7,1000
181347133 1002 EVENT Rules#Timer=7,1
181347179 46 ACT TimerSet_ms,7,1000
181348184 1005 EVENT Rules#Timer=7,1
181348228 44 ACT TimerSet_ms,7,1000
181349231 1003 EVENT Rules#Timer=7,1
181349275 44 ACT TimerSet_ms,7,1000
181350278 1003 EVENT Rules#Timer=7,1
181350324 46 ACT TimerSet_ms,7,1000
181351326 1002 EVENT Rules#Timer=7,1
181351403 77 ACT TimerSet_ms,7,1000
181352405 1002 EVENT Rules#Timer=7,1
181352449 44 ACT TimerSet_ms,7,1000
181353453 1004 EVENT Rules#Timer=7,1
181353498 45 ACT TimerSet_ms,7,1000
181354675 1177 EVENT Rules#Timer=7,1
181354719 44 ACT TimerSet_ms,7,1000
181355722 1003 EVENT Rules#Timer=7,1
181355768 46 ACT TimerSet_ms,7,1000
181356773 1005 EVENT Rules#Timer=7,1
181356818 45 ACT TimerSet_ms,7,1000
181357820 1002 EVENT Rules#Timer=7,1
181357864 44 ACT TimerSet_ms,7,1000
181358866 1002 EVENT Rules#Timer=7,1
181358911 45 ACT TimerSet_ms,7,1000
181359956 1045 EVENT Rules#Timer=7,1
181360000 44 ACT TimerSet_ms,7,1000
181361009 1009 EVENT Rules#Timer=7,1
181361053 44 ACT TimerSet_ms,7,1000
181362058 1005 EVENT Rules#Timer=7,1
181362102 44 ACT TimerSet_ms,7,1000
181363107 1005 EVENT Rules#Timer=7,1
181363151 44 ACT TimerSet_ms,7,1000
181364153 1002 EVENT Rules#Timer=7,1
181364197 44 ACT TimerSet_ms,7,1000
181365200 1003 EVENT Rules#Timer=7,1
181365243 43 ACT TimerSet_ms,7,1000
181366246 1003 EVENT Rules#Timer=7,1
181366290 44 ACT TimerSet_ms,7,1000
181367657 1367 EVENT Rules#Timer=7,1
181367700 43 ACT TimerSet_ms,7,1000
181368896 1196 EVENT Rules#Timer=7,1
181368940 44 ACT TimerSet_ms,7,1000
181370211 1271 EVENT Rules#Timer=7,1
181370257 46 ACT TimerSet_ms,7,1000
181371485 1228 EVENT Rules#Timer=7,1
181371529 44 ACT TimerSet_ms,7,1000
181373184 1655 EVENT Rules#Timer=7,1
on Rules#Timer=8 do
if [Z1#M] = 0 and [Z2#M] = 0 and [Z3#M] = 0 and [SZ#M] = 0
logentry,"No Movement, Power off"
gpio,2,1
TaskValueSet,5,1,-1
logentry,"Power still needed (SZ#M=[SZ#M] Z1#M=[Z1#M] Z2#M=[Z2#M] Z3#M=[Z3#M])"
TimerSet,8,1
on Rules#Timer=7 do
//[VAR#20] second countdown; [VAR#21] direction; [VAR#22] shutter percent
if [VAR#20] >= 0
TimerSet_ms,7,1000
Let,20,[VAR#20]-1
Let,22,[SZ#S]+(100/28)*[VAR#21]
if [VAR#22] < 0 or [VAR#22] > 100
if [VAR#22] < 0
TaskValueSet,1,1,0
TaskValueSet,1,1,100
TaskValueSet,1,1,[VAR#22]
TaskValueSet,1,2,0
Let,20,0
Let,21,0
Let,22,[SZ#S]
SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=%sysname%&SZ=[SZ#M];[SZ#S];
//TaskValueSet,1,2,0
//asyncevent,updatephp
on ControlSZ do
//control?cmd=event,ControlSZ=0
Let,13,%eventvalue%
if [VAR#13] > 0 and [VAR#13] < 100
//open/close percent
Let,10,(28/100)*[VAR#13]
Let,11,(28/100)*[SZ#S]
if [VAR#11] > [VAR#10]
// open a bit
Let,12,[VAR#11]-[VAR#10]
logentry,SZ_o_secs=[VAR#12]
gpio,2,0
TimerSet,8,[VAR#12]+2
delay,250
LongPulse,4,0,[VAR#12]
LongPulse,16,0,[VAR#12]
//TimerSet,7,[VAR#12]
Let,20,[VAR#12]
Let,21,-1
TimerSet_ms,7,1000
TaskValueSet,1,2,1
if [VAR#11] < [VAR#10]
//close a bit
Let,12,[VAR#10]-[VAR#11]
logentry,SZ_c_secs=[VAR#12]
gpio,2,0
delay,250
gpio,16,1
Let,20,[VAR#12]
Let,21,1
TimerSet_ms,7,1000
TaskValueSet,1,2,1
if [VAR#13] = 0
logentry,SZ_o_comp
gpio,2,0
TimerSet,8,28+2
delay,250
LongPulse,4,0,28
LongPulse,16,0,28
//TimerSet,7,28
Let,20,28
Let,21,-1
TimerSet_ms,7,1000
TaskValueSet,1,2,1
if [VAR#13] = 100
logentry,SZ_c_comp
gpio,2,0
TimerSet,8,28+2
delay,250
LongPulse,4,0,28
gpio,16,1
//TimerSet,7,28
Let,20,28
Let,21,1
TimerSet_ms,7,1000
TaskValueSet,1,2,1
if [VAR#13] = 101
logentry,SZ_stop
LongPulse,4,0,0
LongPulse,16,0,0
Let,20,0
if [VAR#13] = 102
//special state
if [VAR#13] = 103
//special state
//TaskValueSet,1,1,[VAR#13]
181320433: Dummy: value 1: -1
181320498: EVENT: Boot#All=-1
181324027: Dummy: value 1: 100.00
181324029: Dummy: value 2: 0
181324053: EVENT: SZ#All=100.00,0
181325982: WD : Uptime 3022 ConnectFailures 0 FreeMem 200848 WiFiStatus WL_CONNECTED ESPeasy internal wifi status: Conn. IP Init
181329413: Dummy: value 1: 0.00
181329415: Dummy: value 2: 0.00
181329416: Dummy: value 3: 0.00
181329418: Dummy: value 4: 0
181329496: EVENT: Z2#All=0.00,0.00,0.00,0
181337838: EVENT: Clock#Time=Thu,16:33
181337863: ACT : asyncevent,updatephp
181338027: HTTP: event,ControlSZ=0
181338324: EVENT: updatephp
181338458: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&ipv4=192.168.10.233&uptime=3022&load=22.35&f
181338883: EVENT: controlsz=0
181338936: ACT : Let,13,0
181339023: ACT : logentry,SZ_o_comp
181339025: SZ_o_comp
181339027: ACT : gpio,2,0
181339029: GPIO : port#2: set to 0
181339034: ACT : delay,250
181339287: ACT : LongPulse,4,0,28
181339290: GPIO : port 4. Pulse set for 28000 ms
181339292: ACT : LongPulse,16,0,28
181339295: GPIO : port 16. Pulse set for 28000 ms
181339297: ACT : Let,20,28
181339301: ACT : Let,21,-1
181339305: ACT : TimerSet_ms,7,1000
181339309: ACT : TaskValueSet,1,2,1
181340307: EVENT: Rules#Timer=7,1
181340353: ACT : TimerSet_ms,7,1000
181340358: ACT : Let,20,28-1
181340394: ACT : Let,22,100.00+(100/28)*-1
181340412: ACT : TaskValueSet,1,1,96.4285714285714
181340492: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;96.43;
181341247: Dummy: value 1: 0.00
181341248: Dummy: value 2: 0.00
181341250: Dummy: value 3: 0.00
181341251: Dummy: value 4: 0
181341263: EVENT: Z3#All=0.00,0.00,0.00,0
181341762: EVENT: Rules#Timer=7,1
181341808: ACT : TimerSet_ms,7,1000
181341813: ACT : Let,20,27-1
181341849: ACT : Let,22,96.43+(100/28)*-1
181341867: ACT : TaskValueSet,1,1,92.8585717337472
181341947: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;92.86;
181342811: EVENT: Rules#Timer=7,1
181342857: ACT : TimerSet_ms,7,1000
181342862: ACT : Let,20,26-1
181342899: ACT : Let,22,92.86+(100/28)*-1
181342917: ACT : TaskValueSet,1,1,89.288572038923
181342997: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;89.29;
181343422: Dummy: value 1: 0.00
181343424: Dummy: value 2: 0.00
181343425: Dummy: value 3: 0.00
181343427: Dummy: value 4: 0
181343511: EVENT: Z1#All=0.00,0.00,0.00,0
181343992: EVENT: Rules#Timer=7,1
181344037: ACT : TimerSet_ms,7,1000
181344042: ACT : Let,20,25-1
181344079: ACT : Let,22,89.29+(100/28)*-1
181344097: ACT : TaskValueSet,1,1,85.7185723440988
181344177: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;85.72;
181345040: EVENT: Rules#Timer=7,1
181345085: ACT : TimerSet_ms,7,1000
181345090: ACT : Let,20,24-1
181345126: ACT : Let,22,85.72+(100/28)*-1
181345144: ACT : TaskValueSet,1,1,82.1485726492746
181345224: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;82.15;
181346087: EVENT: Rules#Timer=7,1
181346131: ACT : TimerSet_ms,7,1000
181346136: ACT : Let,20,23-1
181346173: ACT : Let,22,82.15+(100/28)*-1
181346190: ACT : TaskValueSet,1,1,78.5785729544503
181346298: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;78.58;
181347133: EVENT: Rules#Timer=7,1
181347179: ACT : TimerSet_ms,7,1000
181347184: ACT : Let,20,22-1
181347221: ACT : Let,22,78.58+(100/28)*-1
181347239: ACT : TaskValueSet,1,1,75.0085732596261
181347319: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;75.01;
181348184: EVENT: Rules#Timer=7,1
181348228: ACT : TimerSet_ms,7,1000
181348233: ACT : Let,20,21-1
181348269: ACT : Let,22,75.01+(100/28)*-1
181348286: ACT : TaskValueSet,1,1,71.4385735648019
181348366: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;71.44;
181349231: EVENT: Rules#Timer=7,1
181349275: ACT : TimerSet_ms,7,1000
181349280: ACT : Let,20,20-1
181349316: ACT : Let,22,71.44+(100/28)*-1
181349333: ACT : TaskValueSet,1,1,67.8685738699777
181349413: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;67.87;
181350278: EVENT: Rules#Timer=7,1
181350324: ACT : TimerSet_ms,7,1000
181350330: ACT : Let,20,19-1
181350366: ACT : Let,22,67.87+(100/28)*-1
181350384: ACT : TaskValueSet,1,1,64.2985741751535
181350464: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;64.30;
181351326: EVENT: Rules#Timer=7,1
181351403: ACT : TimerSet_ms,7,1000
181351408: ACT : Let,20,18-1
181351444: ACT : Let,22,64.30+(100/28)*-1
181351462: ACT : TaskValueSet,1,1,60.7285744803292
181351542: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;60.73;
181352405: EVENT: Rules#Timer=7,1
181352449: ACT : TimerSet_ms,7,1000
181352454: ACT : Let,20,17-1
181352491: ACT : Let,22,60.73+(100/28)*-1
181352508: ACT : TaskValueSet,1,1,57.1585709708078
181352588: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;57.16;
181353453: EVENT: Rules#Timer=7,1
181353498: ACT : TimerSet_ms,7,1000
181353503: ACT : Let,20,16-1
181353539: ACT : Let,22,57.16+(100/28)*-1
181353557: ACT : TaskValueSet,1,1,53.5885712759835
181353637: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;53.59;
181354107: Dummy: value 1: 53.59
181354109: Dummy: value 2: 1
181354193: EVENT: SZ#All=53.59,1
181354675: EVENT: Rules#Timer=7,1
181354719: ACT : TimerSet_ms,7,1000
181354725: ACT : Let,20,15-1
181354732: ACT : Let,22,53.59+(100/28)*-1
181354749: ACT : TaskValueSet,1,1,50.0185715811593
181354772: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;50.02;
181355722: EVENT: Rules#Timer=7,1
181355768: ACT : TimerSet_ms,7,1000
181355773: ACT : Let,20,14-1
181355781: ACT : Let,22,50.02+(100/28)*-1
181355798: ACT : TaskValueSet,1,1,46.4485718863351
181355821: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;46.45;
181356240: WD : Uptime 3023 ConnectFailures 0 FreeMem 200616 WiFiStatus WL_CONNECTED ESPeasy internal wifi status: Conn. IP Init
181356773: EVENT: Rules#Timer=7,1
181356818: ACT : TimerSet_ms,7,1000
181356823: ACT : Let,20,13-1
181356831: ACT : Let,22,46.45+(100/28)*-1
181356848: ACT : TaskValueSet,1,1,42.8785721915109
181356872: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;42.88;
181357820: EVENT: Rules#Timer=7,1
181357864: ACT : TimerSet_ms,7,1000
181357869: ACT : Let,20,12-1
181357876: ACT : Let,22,42.88+(100/28)*-1
181357894: ACT : TaskValueSet,1,1,39.3085724966867
181357916: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;39.31;
181358866: EVENT: Rules#Timer=7,1
181358911: ACT : TimerSet_ms,7,1000
181358916: ACT : Let,20,11-1
181358923: ACT : Let,22,39.31+(100/28)*-1
181358940: ACT : TaskValueSet,1,1,35.7385728018624
181358962: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;35.74;
181359413: Dummy: value 1: 0.00
181359414: Dummy: value 2: 0.00
181359416: Dummy: value 3: 0.00
181359417: Dummy: value 4: 0
181359473: EVENT: Z2#All=0.00,0.00,0.00,0
181359956: EVENT: Rules#Timer=7,1
181360000: ACT : TimerSet_ms,7,1000
181360005: ACT : Let,20,10-1
181360041: ACT : Let,22,35.74+(100/28)*-1
181360058: ACT : TaskValueSet,1,1,32.1685731070382
181360138: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;32.17;
181361009: EVENT: Rules#Timer=7,1
181361053: ACT : TimerSet_ms,7,1000
181361059: ACT : Let,20,9-1
181361095: ACT : Let,22,32.17+(100/28)*-1
181361112: ACT : TaskValueSet,1,1,28.5985695975167
181361192: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;28.60;
181362058: EVENT: Rules#Timer=7,1
181362102: ACT : TimerSet_ms,7,1000
181362107: ACT : Let,20,8-1
181362143: ACT : Let,22,28.60+(100/28)*-1
181362160: ACT : TaskValueSet,1,1,25.0285718100412
181362240: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;25.03;
181363107: EVENT: Rules#Timer=7,1
181363151: ACT : TimerSet_ms,7,1000
181363156: ACT : Let,20,7-1
181363192: ACT : Let,22,25.03+(100/28)*-1
181363209: ACT : TaskValueSet,1,1,21.4585721152169
181363289: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;21.46;
181364153: EVENT: Rules#Timer=7,1
181364197: ACT : TimerSet_ms,7,1000
181364202: ACT : Let,20,6-1
181364239: ACT : Let,22,21.46+(100/28)*-1
181364256: ACT : TaskValueSet,1,1,17.8885705130441
181364336: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;17.89;
181365200: EVENT: Rules#Timer=7,1
181365243: ACT : TimerSet_ms,7,1000
181365248: ACT : Let,20,5-1
181365286: ACT : Let,22,17.89+(100/28)*-1
181365338: ACT : TaskValueSet,1,1,14.3185708182199
181365418: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;14.32;
181366246: EVENT: Rules#Timer=7,1
181366290: ACT : TimerSet_ms,7,1000
181366295: ACT : Let,20,4-1
181366331: ACT : Let,22,14.32+(100/28)*-1
181366348: ACT : TaskValueSet,1,1,10.7485711233956
181366428: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;10.75;
181367234: ACT : logentry,'Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)'
181367237: Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)
181367239: ACT : TimerSet,8,1
181367657: EVENT: Rules#Timer=7,1
181367700: ACT : TimerSet_ms,7,1000
181367705: ACT : Let,20,3-1
181367743: ACT : Let,22,10.75+(100/28)*-1
181367790: ACT : TaskValueSet,1,1,7.17857142857143
181367870: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;7.18;
181368283: EVENT: Rules#Timer=8,1
181368485: ACT : logentry,'Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)'
181368488: Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)
181368490: ACT : TimerSet,8,1
181368896: EVENT: Rules#Timer=7,1
181368940: ACT : TimerSet_ms,7,1000
181368946: ACT : Let,20,2-1
181368982: ACT : Let,22,7.18+(100/28)*-1
181369033: ACT : TaskValueSet,1,1,3.60857125691005
181369113: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;3.61;
181369527: EVENT: Rules#Timer=8,1
181369732: ACT : logentry,'Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)'
181369735: Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)
181369737: ACT : TimerSet,8,1
181370211: EVENT: Rules#Timer=7,1
181370257: ACT : TimerSet_ms,7,1000
181370262: ACT : Let,20,1-1
181370298: ACT : Let,22,3.61+(100/28)*-1
181370316: ACT : TaskValueSet,1,1,0.03857132366725
181370396: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;0.04;
181370813: EVENT: Rules#Timer=8,1
181371015: ACT : logentry,'Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)'
181371018: Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)
181371020: ACT : TimerSet,8,1
181371474: Dummy: value 1: 0.00
181371476: Dummy: value 2: 0.00
181371477: Dummy: value 3: 0.00
181371479: Dummy: value 4: 0
181371485: EVENT: Rules#Timer=7,1
181371529: ACT : TimerSet_ms,7,1000
181371534: ACT : Let,20,0-1
181371570: ACT : Let,22,0.04+(100/28)*-1
181371582: ACT : TaskValueSet,1,1,0
181371668: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=1;0.00;
181372093: EVENT: Z3#All=0.00,0.00,0.00,0
181372547: EVENT: Rules#Timer=8,1
181372771: ACT : logentry,'Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)'
181372774: Power still needed (SZ#M=1 Z1#M=0 Z2#M=0 Z3#M=0)
181372776: ACT : TimerSet,8,1
181373184: EVENT: Rules#Timer=7,1
181373277: ACT : TaskValueSet,1,2,0
181373282: ACT : Let,20,0
181373286: ACT : Let,21,0
181373321: ACT : Let,22,0.00
181373362: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&SZ=0;0.00;
181373781: Dummy: value 1: 0.00
181373783: Dummy: value 2: 0.00
181373784: Dummy: value 3: 0.00
181373786: Dummy: value 4: 0
181373797: EVENT: Z1#All=0.00,0.00,0.00,0
181374295: EVENT: Rules#Timer=8,1
181374398: ACT : logentry,'No Movement, Power off'
181374400: No Movement, Power off
181374402: ACT : gpio,2,1
181374404: GPIO : port#2: set to 1
181374406: ACT : TaskValueSet,5,1,-1
181380434: Dummy: value 1: -1
181380500: EVENT: Boot#All=-1
181384027: Dummy: value 1: 0.00
181384028: Dummy: value 2: 0
181384065: EVENT: SZ#All=0.00,0
181385984: WD : Uptime 3023 ConnectFailures 0 FreeMem 200816 WiFiStatus WL_CONNECTED ESPeasy internal wifi status: Conn. IP Init
181389414: Dummy: value 1: 0.00
181389415: Dummy: value 2: 0.00
181389417: Dummy: value 3: 0.00
181389418: Dummy: value 4: 0
181389447: EVENT: Z2#All=0.00,0.00,0.00,0
181397840: EVENT: Clock#Time=Thu,16:34
181397865: ACT : asyncevent,updatephp
181398302: EVENT: updatephp
181398436: ACT : SendToHTTP,192.168.0.250,80,/apcucollector.php?smartswitch=RollladenManager&ipv4=192.168.10.233&uptime=3023&load=57.84&f