Help! It is necessary to reset the variable "TotalCount" every day (Device - Pulse Counter)
Rules -
Code: Select all
On Clock#Time=All,20:00 do
[rain#TotalCount] = 0
endon
On Clock#Time=All,8:00 do
[rain#TotalCount] = 0
endon
Rule does not work
log-
Fri Mar 17 20:00:02 2017: 192.168.0.51: <7>ESP Unit: 0 : EVENT: Clock#Time=Fri,20:00
Fri Mar 17 20:00:02 2017: 192.168.0.51: <7>ESP Unit: 0 : ACT : 1.40 = 0
-
mvn77
- Normal user
- Posts: 12
- Joined: 25 Jan 2017, 21:18
#2
Post
by mvn77 » 18 Mar 2017, 09:14
Bad decision -
Code: Select all
On Clock#Time=All,20:00 do
reboot
endon
On Clock#Time=All,8:00 do
reboot
endon
Do you have any other suggestions?
-
toffel969
- Normal user
- Posts: 469
- Joined: 03 Jan 2017, 10:58
- Location: Germany
#3
Post
by toffel969 » 18 Mar 2017, 10:54
Have you tried TaskValueSet command?( store variable in Dummy device, and 2.. task) then read dummy rather than sensor value
Like
On pulse#total do
TaskValueSet 2,1,[pulse#total]
End on
On Clock #Time=all, 20:00 do
TaskValueSet 2,1,0
Endon
Domoticz on Raspi 2 -- 14 ESP units (hacked Sonoff,NodeMCUs, Wemos, self-built units) running with RC140- Mega 2.0.0 dev8
-
mvn77
- Normal user
- Posts: 12
- Joined: 25 Jan 2017, 21:18
#4
Post
by mvn77 » 18 Mar 2017, 12:01
I thought. But with the next record, he will write down the "pulse#total" value into the variable.
How much I understood in rules it is impossible to work with variables - to subtract, to multiply ....
-
paxi
- Normal user
- Posts: 121
- Joined: 02 Feb 2017, 00:48
- Location: Germany
#5
Post
by paxi » 18 Mar 2017, 18:04
mvn77 wrote: ↑18 Mar 2017, 09:14
Bad decision -
Code: Select all
On Clock#Time=All,20:00 do
reboot
endon
On Clock#Time=All,8:00 do
reboot
endon
Do you have any other suggestions?
What happens? Bootloop for a minute I guess. In this case a workaround is to set a timer and reboot when it's 20:01.
You
can do basic calculations in rules like this:
Code: Select all
TaskValueSet 4,3,[test#a]-[test#b]
So store your a bias-pulsecount once a day in one variable, substract that from the actual pulsecount into another dummyvalue and publish this.
-
mvn77
- Normal user
- Posts: 12
- Joined: 25 Jan 2017, 21:18
#6
Post
by mvn77 » 19 Mar 2017, 12:06
Thank you!!!!!!
-
mvn77
- Normal user
- Posts: 12
- Joined: 25 Jan 2017, 21:18
#7
Post
by mvn77 » 19 Mar 2017, 18:59
Can create a rule for calculating RAINRATE for DOMOTICZ? RAINRATE = amount of rain in last hour
-
paxi
- Normal user
- Posts: 121
- Joined: 02 Feb 2017, 00:48
- Location: Germany
#8
Post
by paxi » 20 Mar 2017, 00:27
Always a joy.
"Hourly rain" would be easy with the same principle using a timer that triggers every 60 minutes but that would only provide a measurement for every full hour. An instant (every minute) "last 60 minutes" would require to store 60 values and awefullly hacky rules- too much for espeasy - as mentioned earlier I don't use domoticz nor know its cababilities but think this kind of statisic is definately a job for the controler.
You could compromise something with 15 minute intervalls using the 4 availible values of a single dummy device, still a lot of fiddling though.
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#9
Post
by novembre62 » 10 May 2019, 15:49
Hi!
I take these old posts to be helped:
sorry but I'm very inexperienced
I would like to reset my pulse counter variable at 00:01 every day
"Total" with the TaskValueSet rule
"Sensors": [
{
"TaskName": "counter",
"Count": 0.00,
"Total": 2591.75, <<<<<<<<<<<< THIS
"Time": 27470.00
},
{
"TaskName": "outside temperature",
"Temperature": 21.19
}
but I don't understand how to do it ... someone can help me
thank you
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#10
Post
by grovkillen » 10 May 2019, 16:47
Use rule and the command TaskValueSet.
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#11
Post
by grovkillen » 10 May 2019, 16:58
Code: Select all
On Clock#Time=All,00:01 Do
TaskValueSet,TaskNo,ValueNo,Value
EndOn
If your device is on task number 4 (as an example) and the total is on value number 3 your rule would be looking like this:
Code: Select all
On Clock#Time=All,00:01 Do
TaskValueSet,4,3,0
EndOn
And that is already explained further up in this topic.
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#12
Post
by novembre62 » 10 May 2019, 19:48
Thanks for the reply.
I apologize if I ask a trivial question, but I am inexperienced ..
how can I then have the new value as a json output?
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#13
Post
by grovkillen » 10 May 2019, 20:06
To trigger the value change event you can do the same but change the command to TaskValueSetAndRun.
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#14
Post
by novembre62 » 10 May 2019, 21:35
I entered the "TaskValueSetAndRun" command with rule
On Clock # Time = All, 21: 28 do
TaskValueSetAndRun, 1,2,0
Endon
but the "Total" value of the pulser counter device does not change
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#15
Post
by grovkillen » 11 May 2019, 10:12
Don't have spaces in the event name!
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#16
Post
by novembre62 » 11 May 2019, 14:26
there are no spaces
in image my device
https://drive.google.com/file/d/1ZiPhKf ... dgXug/view
then
On Clock#Time=All,12:09 Do
TaskValueSetAndRun,1,2,0
EndOn
it's correct ?
the "TaskValueSetAndRun" command, should change the "Total" value of my device to 0 at the set time and then continue counting until the next set time ?????
Do not do anything else ... I read in the tutorial rules that a Dummy Device needs ... but I don't know how to do it
I use the value of my "Total" device as a JSON output, which I read in a monitoring system (Metern) in this way
http://192.168.1.150/json?tasknr=1
It is a water meter and I would like to reset the value every day at 00:01
I apologize for my inexperience
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#17
Post
by grovkillen » 11 May 2019, 14:35
Maybe try the TaskValueSet followed be a TaskRun instead...
Code: Select all
...
TaskValueSet,1,2,0
TaskRun,1
...
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#18
Post
by grovkillen » 11 May 2019, 14:38
If that isn't working it might be a bug.
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#19
Post
by novembre62 » 11 May 2019, 14:41
I tried but it doesn't work
log:
60867434: ACT: TaskValueSet, 1,2,0
60867446: ACT: TaskRun, 1
60867475: EVENT: counter # Count = 0.00
60867503: EVENT: counter # Total = 344.75
60867536: EVENT: counter # Time = 1245007.00
60876994: WD: Uptime 1011 ConnectFailures 0 FreeMem
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#20
Post
by novembre62 » 11 May 2019, 14:42
Total value does not change
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#21
Post
by grovkillen » 11 May 2019, 14:43
Ok, I guess that TaskValueSet is the command not working then. Until we have fixed it you may do a reboot once at 00:01?
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#22
Post
by novembre62 » 11 May 2019, 14:45
that's what I already do, reboot at 00:01, but I'd like to avoid this
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#23
Post
by novembre62 » 11 May 2019, 14:47
in the post above I read:
TaskValueSet 4.3, [test # a] - [test # b]
but I didn't understand what to do
-
grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
-
Contact:
#24
Post
by grovkillen » 11 May 2019, 14:57
The other example you posted is to show how you can do calculations. That's not what you're asking about. It's a bug and we should fix it. But in the meantime, do the reboot.
-
TD-er
- Core team member
- Posts: 8794
- Joined: 01 Sep 2017, 22:13
- Location: the Netherlands
-
Contact:
#26
Post
by TD-er » 11 May 2019, 21:44
There still is a space in the line of the rules
And the suggestion made by Jimmy to do the reboot will probably not work (anymore) in the more recent builds.
I (quite recently) fixed a bug, which does now keep track of the last values of plugins after a reboot. (as long as the board was powered)
So I expect the plugin to continue counting after a crash or reboot.
-
Domosapiens
- Normal user
- Posts: 307
- Joined: 06 Nov 2016, 13:45
#27
Post
by Domosapiens » 12 May 2019, 01:06
My suggestion,
at 00.01
read the value
and
subtract that value
30+ ESP units for production and test. Ranging from control of heating equipment, flow sensing, floor temp sensing, energy calculation, floor thermostat, water usage, to an interactive "fun box" for my grandson. Mainly Wemos D1.
-
novembre62
- Normal user
- Posts: 30
- Joined: 10 May 2019, 15:39
- Location: italy
#28
Post
by novembre62 » 23 Aug 2019, 18:51
.....My suggestion,
at 00.01
read the value
and
subtract that value.....
.......I do not know how to do...
I can get help
thank you