Abnormalities when using an MCP23017 as out-/input
Micha_he
#1 Post by Micha_he » 05 Jul 2021, 11:21
I've configured a ESP12F with a MCP23017, 6 input-/output-devices. All set (MCPGpio,x,0) to 0 at boot and non of my rules is executed.
At the MCP-ports is an optucupler connected, with a 1,5k resistor, second side of the optocupler is connected to ground.
But at irregular intervals the signal on the 6 devices is change to 1 for less than 1sec, always a different port alternately.
Is it a problem to use the MCP-port as output (control the valve) & input (to publish the actual state) at the same time?
Should I use another configuration ?
In my opinion, the same configuration worked with firmware from last year without any problems.
I've also already provided the inputs with an additional pull-down resistor, no changes.
Here's the part from the log:
80253494: EVENT: Clock#Time=Mon,11:11
80253698: EVENT: Clock#Time=Mon,11:11 Processing time:204 milliSeconds
80282040: WD : Uptime 1338 ConnectFailures 0 FreeMem 15672 WiFiStatus WL_CONNECTED 3 ESPeasy internal wifi status: Conn. IP Init
80282933: LoopStats: shortestLoop: 922 longestLoop: 896405 avgLoopDuration: 1430.00 loopCounterMax: 32537 loopCounterLast: 20784
80282933: Scheduler stats: (called/tasks/max_length/idle%) 20784/1889/16/66.73
80288287: MCP : Port=5 State=1 Output value=1
80288300: MQTT : Bewaesserung/Ventil5/Status 1
80288306: EVENT: Ventil5#Status=1
80288515: EVENT: Ventil5#Status=1 Processing time:209 milliSeconds
80288532: MCP : Port=5 State=0 Output value=0
80288544: MQTT : Bewaesserung/Ventil5/Status 0
80288551: EVENT: Ventil5#Status=0
80288843: EVENT: Ventil5#Status=0 Processing time:292 milliSeconds
Thanks, Micha.
Re: Abnormalities when using an MCP23017 as out-/input
#2 Post by TD-er » 05 Jul 2021, 12:08
The last part makes me wonder; "which ground?"
If it is the same GND as the ESP circuit, then why use optocouplers?
What does it control? You mention a valve, which sounds like a solenoid.
But what's inbetween the solenoid and the optocoupler?
Is the GND of the circuit switching the valves and the GND of ESP actually connected and if so, is it really needed?
Based on the logs, it looks like the logic state of the MCP does change, but with only a connected LED, that's not making sense (except for bugs in the firmware of course)
So I wonder if you may have unexpected currents in your circuit which may induce some strange spikes on the MCP inputs.
Micha_he
#3 Post by Micha_he » 05 Jul 2021, 13:47
Yes, ground is the same. I use this mosfet driver: https://www.pollin.de/p/bausatz-mosfet- ... 00w-810329 to control a 12v solenoid.
The state at the MCP-pin can't change! Only the led from the optocupler is connected. GND from ESP and GND from the solenoid are not connected to each other.
#4 Post by TD-er » 05 Jul 2021, 13:51
Does this state flipping happen when a valve has switched?
#5 Post by Ath » 05 Jul 2021, 14:01
What length are the wires between the MCP23017 and your mosfet board?
What other wiring is near those wires (possibly causing cross-talk spikes?)
#6 Post by TD-er » 05 Jul 2021, 14:07
Also do you have diodes over the solenoids? (some mosfet do have them included)
Micha_he
#7 Post by Micha_he » 05 Jul 2021, 14:32
TD-er wrote: 05 Jul 2021, 13:51 Does this state flipping happen when a valve has switched?
No, possibly rather if it wasn't switched for some time.
Ath wrote: 05 Jul 2021, 14:01 What length are the wires between the MCP23017 and your mosfet board?
About 8-10cm. No other wiring only the wires to these 4 inputs and maybe 1 or 2 wires from the default MCP schematic (address, SDA, SCL).
TD-er wrote: 05 Jul 2021, 14:07 Also do you have diodes over the solenoids? (some mosfet do have them included)
These are already on the MOSFET driver.
And the ESP & MCP is in standby (no solenoid is changed) while I can see this problem in the logs.
#8 Post by Ath » 05 Jul 2021, 15:06
Micha_he wrote: 05 Jul 2021, 11:21 In my opinion, the same configuration worked with firmware from last year without any problems.
Any version/release that you know that it is working as expected (without intermittent triggers)? There have been changes to the PCF/MCP plugins, AFAICS, though I can't validate what could be a cause of this report.
Micha_he
#9 Post by Micha_he » 05 Jul 2021, 15:23
It's a little bit complucated... I've update this device a few times, before I see this problem.
If I found some time while the next days, I flash some older versions. But these tests take some time, because this state-flip does not occur immediately.
Zodiac69
#10 Post by Zodiac69 » 05 Jul 2021, 20:26
Hi Micha_he
It might be a silly question but, have you pulled your MCP23017 address lines to the same GND as your ESP?
For Address 1, all address lines of the MCP should be tied to GND - 0V
I had a case where the MCP lines were floating, it worked 100% until there was a relay switched.
The unit would then have strange behaviour and sometime even drop communications.
Any "noise" would make an output port switch on or make the unit crash.
Micha_he
#11 Post by Micha_he » 05 Jul 2021, 22:09
Yes, all address-lines are connected to GND, ESP-GND and MCP-GND is the same.
Micha_he
#12 Post by Micha_he » 06 Jul 2021, 13:10
I'm back to 20181231, in steps of ~ 1/2 year.
The problem still exists in all versions!
#13 Post by TD-er » 06 Jul 2021, 13:19
So it is a bit more likely this is caused by something in your circuit or use case. (still possible it is a bug, but you're the first to mention it)
Micha_he
#14 Post by Micha_he » 06 Jul 2021, 13:58
I'm currently create a test setup, with another ESP and MCP, but only with resistors on the ports. We'll see...
#15 Post by TD-er » 06 Jul 2021, 14:04
The optocouplers, how are the LEDs from it being used?
Does the MCP source the power or does it connect the LED to GND?
The LED does have a voltage drop, so maybe that's the reason it may trigger something?
Maybe it is better to let the MCP drain the current of the LEDs?
Micha_he
#16 Post by Micha_he » 06 Jul 2021, 14:56
I hope I haven't misunderstood you now...
Yes, that's how it's connected. MCP drive the signal and the LED is connected to GND. Look at this input-circuit:
[attachment=0]RB4-4_In.jpg[/attachment
#17 Post by TD-er » 06 Jul 2021, 15:39
My electronics knowledge is just based on reading and experimenting, so I might be wrong.
Imagine the wires do pick up some noise.
When using a simple resistor, the noise induced voltage will not exceed a few mV as you need to have quite some energy to generate enough current to get a higher voltage over this resistor.
But the amount of current through a diode can be a lot less to get a voltage drop of a few Volt, depending on the diode. (the color of the LED)
So maybe it is better to have a much lower voltage drop there, by using a transistor to switch the LED in the optocoupler?
Then the max. induced voltage over the IO-pin will likely be at 0.7V max.
Micha_he
#18 Post by Micha_he » 07 Jul 2021, 13:38
We can exclude the optocouplers as the cause, because I disconnected them and replaced it with a simple pull-down-resistor.
But the problem still exists :(
The test-setup (I mean, same handmade config, same rules,same firmware but ESP is Wroom02-1M instead of ESP12F-4M) works without errors !
#19 Post by TD-er » 07 Jul 2021, 13:48
Could it be an issue of I2C communication which may be affected?
Have you tried to add some pull-up resistors to both I2C pins? (e.g. 4k7)
How is the ESP powered? And the MCP?
Micha_he
#20 Post by Micha_he » 07 Jul 2021, 14:06
SDA & SCL have pullup's with 4,7k.
The power-supply is a Hi-Link PM03 with a 220µF cap at the outside, for ESP & MCP. ESP & MCP have additional a cap of 100nF near it.
Next week I look at the power-supply with a oscilloscope.
#21 Post by TD-er » 07 Jul 2021, 14:35
Maybe also have a good look at the quality of the GND.
mrwee
#22 Post by mrwee » 08 Jul 2021, 11:10
Just a small comment. My recent valve-project is based on a orignal Wemos D1 mini Pro and a MCP23017 used for I/O and I don't see any issues like you're describing.
Was running "ESP_Easy_mega_20210503_normal_ESP8266_4M1M", but I'm on "ESP_Easy_mega_20210615_normal_ESP8266_4M1M" now, since the Wi-Fi issues are hitting me quite bad.
Hope you find the root-cause
#23 Post by ThomasB » 08 Jul 2021, 18:31
Try longer debounce times. And perhaps enable Safe Button to see if it helps.
Micha_he
#24 Post by Micha_he » 08 Jul 2021, 21:51
Debounce time of 250ms (more isn't available) didn't help.
'Safe button' I'll try out... First I'll check the power supply.
Micha_he
#25 Post by Micha_he » 21 Jul 2021, 08:10
These are the things, which were unsuccessful:
Check Hi-Link 3,3V power supply: Interference frequency ~ 100kHz, ~80mV. No abnormalities.
Another 3,3V power supply
Additional 470µF capacitor at 3,3V power supply (interference frequency ~ 100kHz, ~80mV)
Reduce the SCL/SDA pullup from 4,7k to 1,8k, because the rise-time was to long (900ns) for 400k-I2C
Thicker wire for SCL/SDA
Another position for SCL/SDA-wiring
Reduce I2C-clock to slow
None of this brought any improvement. Now I'll test with enabled 'Safe button'...
Remark: The duration for this wrong/unclear signal change is always ~ 250ms !?
Question: If the I2C-communication isn't successful or has errors, we see this in the log?
#26 Post by TD-er » 21 Jul 2021, 15:19
Not sure if you will see anything in the logs, but if the I2C hangs you can see this in an I2C scan which will return an error on each possible address.
Also for testing you could try to reduce the I2C frequency if you're having doubts on stability at higher frequency.
Are you using long cables if you do see a rise time of 900 ns?
Lowering the pull-up may increase the rise time of the 2 I2C lines, but the connected devices must also be capable to source the higher current and it should not affect the power supply to the chip.
It is a good practice to add 100 nF capacitors as close as possible to the power pins of each I2C chips.
Micha_he
#27 Post by Micha_he » 21 Jul 2021, 15:45
No long cables. The ESP and the MCP are on the same PCB. Wires (https://de.wikipedia.org/wiki/F%C3%A4deltechnik) are ~ 6-7cm.
I can't explain where the high capacity comes from. Only ESP, 6-7cm wiring and the MCP. Pullup was 4,7k and the rise-time ~900ns ???
Reduce the I2C hasn't anything improved, as I already write...
Both chips have their 100nF capacitor !
#28 Post by TD-er » 21 Jul 2021, 16:51
For 400 kHz you could still use 900 ns as the period is 2.5 usec, so you're below 50%.
What do you count as the level above which you stop measuring?
And what is the fall-time? (measured at the ESP and at the chip)
Can you experiment with a setup with thicker wires?
Capacitance is only one explanation of the slow rise time.
Micha_he
#29 Post by Micha_he » 21 Jul 2021, 18:13
This is a statement from the specification: The rise-time of SDA/SCL to be a maximum of 300 ns in "Fast-mode”
You mean the level to stop the measuring the rise-time? 70% of Vcc (3,3V) = ~2,3V
Rise-time with 4,7k (resulution 2µs):
Rise-time with 1,8k (resultion 1µs):
I've tried thicker wires. No improvement. Same rise-time.
#30 Post by ThomasB » 21 Jul 2021, 21:17
Do you mean that for each optocoupler, the MCP's input and output pin is the same one? If this is how it is wired then the pin read isn't from the *latched* output state. Instead, the I/O pin becomes Hi-Z (input mode) and then it reads the "open" (un-driven) circuit logic level. So whatever circuitry is connected determines the logic level that is read, not the MCP output state.
In your case the Opto cathodes are pulled high. So even if the MCP pin was driven low, there is a chance that the level might be logic high on a read. The chance of a high level depends on the rise time of the newly open signal path. BTW, Pulldown/Pullup resistor band-aides are not a reliable solution since you are interested in the MCP's latched output state, not the logic level seen on the un-driven pin.
Assuming that the same MCP pin is currently doing the reading and writing, I propose two alternate ideas:
(1) Only use the MCP to drive the outputs (no reads). Store the output states in internal vars (%v%). Instead of reading the I/O pin, read the saved system's internal var states. If you need values that are retained after a warm reset then use dummy plugin vars instead.
(2) Use separate MCP pins to read the output pins. That is to say, one set of pins for output-only, another set for input-only.
FWIW, the MCP23017 supports two different pin read modes. It can read either the logic level on the I/O pin (GPIOx registers) or the output latch state (OLATx registers). ESPEasy currently reads only the GPIOx states. Reading the OLATx would require enhancing ESPEasyGPIO.cpp code. All possible (send hugs & beers to developers), but the internal var workaround is a practical solution.
Final thoughts. I am not sure if your issue is related to my suspected fault that's explained above. But it's high on the list of reasons for the unreliable pin reading behavior.
Micha_he
#31 Post by Micha_he » 22 Jul 2021, 08:42
With "out-/input at the same" I mean:
Out = I set the output with the MCPGPIO-command in my rules
In1 = The MCP GPA0-5 are also configured as switch-input-task, with a connection to my MQTT-broker. Here's my problem: I receive high-level for ~250ms at my broker. Always another input, and the the level at the MCP-pins are not changed.
In2 = The state of this switch-input-tasks is additional published via rules
Here's my schematic (current R4/R5 are 1k8):
This is my configuration:
@ThomasB: Your idea #2 is worth considering. I'd also already thought of using the GPB for this purpose.
Micha_he
#32 Post by Micha_he » 22 Jul 2021, 12:00
First results from the "Safe-Button" test:
I've change the first 3 MCP-Switch-Input's to Safe-Button activated, last 3 not. Within the last 16h, only the last 3 task's were change to 1 :P
Micha_he
#33 Post by Micha_he » 22 Jul 2021, 17:59
I was probably too fast... :(
Now I get a state = 4 from my 3 changed MCP-switch-inputs.
Edit: Aha, now I mean I've understand the value of "4" (documentation for the "Safe-Button" doesn't point to this value). The value of "4" mean, the length of the signal was too short, or ?
Micha_he
#34 Post by Micha_he » 11 Sep 2022, 11:55
I continue to have problems with my MCP outputs. I've change the config to internal MCP-commands (no MCP Devices are configured).
This is part of my boot rule:
on System#Boot do
  MCPmodeRange,1,7,0  // 1-7 als Ausgang
  MCPGPIOrange,1,7,0  // Ventil1-7 AUS
  MonitorRange,MCP,1,7
The penultimate line is the interesting one! Where does the MCP-event come from, if no MCPGpio-command was sent by any rule?
166155075: EVENT: AutoPrgStartStop=1
166155148: ACT : TaskValueSetAndRun,3,1,1
166155154: Dummy: value 1: 1
166155156: Dummy: value 2: 0
166155157: Dummy: value 3: 0
166155159: Dummy: value 4: 0
166155171: ACT : AsyncEvent,AutoPrgWeiter
166155255: EVENT: Programm#lfdPrg=1
166155272: ACT : Publish,Bewaesserung/Programm/LfdPrg,1
166155291: EVENT: Programm#aktSek=0
166155303: ACT : Publish,Bewaesserung/Programm/AktSek,0
166155316: EVENT: Programm#=0
166155329: EVENT: Programm#=0
166155343: EVENT: AutoPrgWeiter
166155386: ACT : Let,9,1
166155463: ACT : TaskValueSetAndRun,3,2,1
166155469: Dummy: value 1: 1
166155470: Dummy: value 2: 1
166155472: Dummy: value 3: 0
166155476: Dummy: value 4: 0
166155491: ACT : AsyncEvent,VentilSchalten=1,1
166155495: ACT : Let,9,0
166155577: EVENT: Programm#lfdPrg=1
166155592: ACT : Publish,Bewaesserung/Programm/LfdPrg,1
166155611: EVENT: Programm#aktSek=1
166155623: ACT : Publish,Bewaesserung/Programm/AktSek,1
166155636: EVENT: Programm#=0
166155651: EVENT: Programm#=0
166155664: EVENT: VentilSchalten=1,1
166155676: ACT : Let,1,1
166155680: ACT : AsyncEvent,PumpeUndNT=1
166155684: ACT : MCPGpio,1,1
166155689: MCP : port#1: set to 1
166155701: ACT : Let,7,15*100*.6
166155734: ACT : Timerset,1,900
166155814: EVENT: PumpeUndNT=1
166155828: ACT : Publish,SW011/cmd,'event,Schalten=1'
166155837: ACT : Gpio,13,1
166155840: GPIO : port#13: set to 1
166155857: EVENT: MCP#1=0
166155867: ACT : Publish,Bewaesserung/Ventil1/Status,0
Firmware is actual from action build 20220909.
#35 Post by TD-er » 11 Sep 2022, 12:36
You're monitoring the pins, so if the pin state changes, then an event is fired (or at least that's how it was intended to be)
But first things first...
How sure are you that the log entry you're looking at actually is what's happening <now> and not like seconds or minutes ago?
The reason I'm asking is that on ESP32 (without the rules cache enabled) the rules processing was so slow, events were added to the queue and I got to see essentially a slow replay of events instead of acting on actual events.
Also using asyncevents is great from a resources perspective, but it might make things a bit harder to debug since direct events might be handled before queued events.
Not saying you should move to using event commands over async events, but more that you really need to be sure about the order of events.
Another thing to keep in mind is that even though you might set a MCP pin high, its actual state of the pin might not be high as it may be pulled down harder than the MCP may pull it up. (e.g. when shorted to GND)
This way the logic state from the monitoring view point may have changed as you're setting it high and when looking it is low (again?)
Micha_he
#36 Post by Micha_he » 11 Sep 2022, 13:09
TD-er wrote: 11 Sep 2022, 12:36 How sure are you that the log entry you're looking at actually is what's happening <now> and not like seconds or minutes ago?
I've followed the log in real time and also multiple times.
TD-er wrote: 11 Sep 2022, 12:36 Also using asyncevents is great from a resources perspective, but it might make things a bit harder to debug since direct events might be handled before queued events.
No other MCPGpio-Command is used (no other rule is execute is the test), I've checked the log completely.
TD-er wrote: 11 Sep 2022, 12:36 Another thing to keep in mind is that even though you might set a MCP pin high, its actual state of the pin might not be high as it may be pulled down harder than the MCP may pull it up. (e.g. when shorted to GND)
You can see the circuit in post #16. It's an optocoupler over a 1.5k resistor connected. No other connections. And all output's have the same problem, but not always.
Micha_he
#37 Post by Micha_he » 17 Sep 2022, 15:02
It seems, that I located the problem.
It's not one (or some) output that reset to 0, but all ! My guess, the MCP23017 performed a reset :cry:
The MCP-reset-line was connected to Vcc via a 10k resistor and have a 100nF capacitor.
Now I've reduced the resistor to 4.7k and added a 1µF Elko to the reset-line.
Currently I can't reproduce the error :)
Users browsing this forum: No registered users and 100 guests
