I have a problem with my soil moisture sensor (P47), I have connected it to ESP board with a 5 mt. cable.
If I use a ESP01 board it's ok and work fine but with ESP07, ESP12 or NODEMCU board id don't work at all.
I'm sure the cause is cable lenght, if I short it I have no problem.
I tried to use GPIO4 - GPO5 anf GPIO0-GPIO2 on ESP07 and NODEMCU device, but all is the same...ESP don't find I2C device.
GIT version is mega-20180606 for all devices, do someone have some advice to fix this?
Thank
Soil moisture with long cable...
Moderators: grovkillen, Stuntteam, TD-er
Re: Soil moisture with long cable...
Try to use a twisted pair cable with shielding. Make sure to connect the shielding to GND.albertobonati wrote: ↑11 Jun 2018, 21:13 Hi.
I have a problem with my soil moisture sensor (P47), I have connected it to ESP board with a 5 mt. cable.
If I use a ESP01 board it's ok and work fine but with ESP07, ESP12 or NODEMCU board id don't work at all.
I'm sure the cause is cable lenght, if I short it I have no problem.
I tried to use GPIO4 - GPO5 anf GPIO0-GPIO2 on ESP07 and NODEMCU device, but all is the same...ESP don't find I2C device.
GIT version is mega-20180606 for all devices, do someone have some advice to fix this?
Thank
Also, when using standard network cable (CAT5-7) you will have 8 wires + shield.
Do:
- run SCA and SDL each together with a GND in a twisted pair of wires.
Do Not:
- run SCA and SDL in the same twisted pair
- Connect multiple wires together. More Cu will increase capacitance, which is THE limiting factor in I2C .
Next step would be a stronger (fewer ohms) pullup resistors.
Last resort are I2C extenders
Domoticz on Raspi 2 -- 14 ESP units (hacked Sonoff,NodeMCUs, Wemos, self-built units) running with RC140- Mega 2.0.0 dev8
-
- Normal user
- Posts: 40
- Joined: 13 Dec 2016, 15:25
Re: Soil moisture with long cable...
Hi...thanks a lot.
I'll try !!!
Regards
Alberto