I try to use a Sonoff POW (R2 v1.0 with mega-20180826) for failure monitoring of a drainage pump. The pump is allways voltage supplied and switches itself on/off dependend on the water level. If the pump is working the Sonoff recognize the used current and even calculates the energy but I don't manage to use this for triggering a command like:
On Pumpe#Current>0 do ...
If I use an other device from my list everything works fine e.g.:
On Button#pressed>0 do ...
My settings for devices are:
Task: 1
Enabled: ✔
Device: Energy (AC) - CSE7766 [TESTING]
Name: Pumpe
GPIO:
Values: Voltage: 239.15 Power: 36.90 Current: 0.16 Pulses: 12577.00
Task: 2
Enabled: ✔
Device: Switch input - Switch
Name: Button
GPIO: GPIO-0
Values: pressed: 1
Might this be somehow connected to the selected device type for current measurement 'Energy (AC) - CSE7766 [TESTING]'?
Any suggestions?
Sonoff POW rule trigger for Current / Power
Moderators: rtenklooster, Voyager, BertB, Stuntteam
Forum rules
You have entered the experimental forum, beware!!!
You have entered the experimental forum, beware!!!
-
- Normal user
- Posts: 11
- Joined: 02 Aug 2018, 12:36
- grovkillen
- Core team member
- Posts: 3621
- Joined: 19 Jan 2017, 12:56
- Location: Hudiksvall, Sweden
- Contact:
Re: Sonoff POW rule trigger for Current / Power
If you look in the log, what do you see?
ESP Easy Flasher [flash tool and wifi setup at flash time]
ESP Easy Webdumper [easy screendumping of your units]
ESP Easy Netscan [find units]
Official shop: https://firstbyte.shop/
Sponsor ESP Easy, we need you

ESP Easy Webdumper [easy screendumping of your units]
ESP Easy Netscan [find units]
Official shop: https://firstbyte.shop/
Sponsor ESP Easy, we need you



-
- Normal user
- Posts: 11
- Joined: 02 Aug 2018, 12:36
Re: Sonoff POW rule trigger for Current / Power
When I connect a device to drain power there is no trigger reaction. It seemed that the log is frozen. After refresh for the log I can see other trigger events (e.g. for pressing a Button) but never for the change of Power / Current.
-
- Normal user
- Posts: 11
- Joined: 02 Aug 2018, 12:36
Re: Sonoff POW rule trigger for Current / Power
I just found out that I'm not the only one with this problem:
https://letscontrolit.com/forum/viewtop ... 6&start=53
I have solved my problem by following the advice to change the default value '0' for 'Interval' of the 'Data Acquisition' in the 'Task Settings' for device 'Energy (AC) - CSE7766 (POW r2) [TESTING]'.
At an interval of 6s the trigger works fine and there is no frozen LOG anymore.
What can I do to prevent the next user from stepping into the same trap?
Is it worth it to write a wiki article (for example, behind the question mark on the configuration page) or should it be reported in Github as an error / false default (and will hopefully be changed in the near future)?
https://letscontrolit.com/forum/viewtop ... 6&start=53
I have solved my problem by following the advice to change the default value '0' for 'Interval' of the 'Data Acquisition' in the 'Task Settings' for device 'Energy (AC) - CSE7766 (POW r2) [TESTING]'.
At an interval of 6s the trigger works fine and there is no frozen LOG anymore.
What can I do to prevent the next user from stepping into the same trap?
Is it worth it to write a wiki article (for example, behind the question mark on the configuration page) or should it be reported in Github as an error / false default (and will hopefully be changed in the near future)?