Measure current ACS712 and ADS1115 are not working properly
Moderators: grovkillen, Stuntteam, TD-er
Measure current ACS712 and ADS1115 are not working properly
Hi there,
I would like to use the ADS1115 to record the analog signal of the ACS712 current sensor a little more precisely.
With the rules I cannot offset the A0 port with the A1 port.
Only one value is ever assigned to a variable.
The offsetting by the ADS115 A1-A0 works, but I cannot calculate an average.
The transfer via task device to dummy is only possible with one port.
What am I doing wrong?
ESP_Easy_mega_20211005_test_B_beta_ESP8266_4M1M
ADS1115 # A0 // AIN0 - GND //FS6.144V
ADS1115 # A1 // AIN1 - GND //FS6.144V
ADS1115 # A0_A1 // AIN0 - AIN1 (differential)
Greetings Dondolo
I would like to use the ADS1115 to record the analog signal of the ACS712 current sensor a little more precisely.
With the rules I cannot offset the A0 port with the A1 port.
Only one value is ever assigned to a variable.
The offsetting by the ADS115 A1-A0 works, but I cannot calculate an average.
The transfer via task device to dummy is only possible with one port.
What am I doing wrong?
ESP_Easy_mega_20211005_test_B_beta_ESP8266_4M1M
ADS1115 # A0 // AIN0 - GND //FS6.144V
ADS1115 # A1 // AIN1 - GND //FS6.144V
ADS1115 # A0_A1 // AIN0 - AIN1 (differential)
Greetings Dondolo
- Attachments
-
- Rules.JPG (17.99 KiB) Viewed 7865 times
-
- Log.JPG (41.22 KiB) Viewed 7865 times
-
- Device.JPG (61.01 KiB) Viewed 7865 times
-
- A0-A1.JPG (92.26 KiB) Viewed 7865 times
-
- Device.JPG (61.01 KiB) Viewed 7865 times
Re: Measure current ACS712 and ADS1115 are not working properly
You should not try to name your Value "ADS1115#A0_A1", that's surely going to mess up somewhere unexpected.
And also, each task must have a unique name, they should not all be named ADS1115 !
And do you have different I2C addresses set for each task? That's also kind of required for the ADS1115 to work correctly, as when the all try to address the same module at nearly the same time, it will have a similar effect as running the unit at too high I2C clock speed.
Then your rule(s): When trying to access multiple values of a task in 1 event, you should better enable 'Single event with all values' and use %eventvalue1%, %eventvalue2% etc.
And also, each task must have a unique name, they should not all be named ADS1115 !
And do you have different I2C addresses set for each task? That's also kind of required for the ADS1115 to work correctly, as when the all try to address the same module at nearly the same time, it will have a similar effect as running the unit at too high I2C clock speed.
Then your rule(s): When trying to access multiple values of a task in 1 event, you should better enable 'Single event with all values' and use %eventvalue1%, %eventvalue2% etc.
/Ton (PayPal.me)
Re: Measure current ACS712 and ADS1115 are not working properly
Hello Ath, thanks for the quick reply.
The first part has already helped, thanks!
Now looks like this:
That was just for testing
Another question, how do I determine the correct current value in Amper with the formula?
My formula doesn't work, a voltage divider is installed on A1 that halves the voltage.
The first part has already helped, thanks!
Now looks like this:
I didn't understand that, the ADS1115 sensor only has one IC2 address.And do you have different I2C addresses set for each task? That's also kind of required for the ADS1115 to work correctly, as when the all try to address the same module at nearly the same time, it will have a similar effect as running the unit at too high I2C clock speed.
That was just for testing
Code: Select all
On ADS1115A0#A0 do
let,1,[ADS1115A0#A0]
let,2,[ADS1115A1#A1]
let,3,[VAR#1]-[VAR#2]
TaskValueSet,8,1,[VAR#2]
TaskValueSet,8,2,[VAR#1]-[VAR#2]
endon
Code: Select all
%value%/0.185
- Attachments
-
- A1A0.JPG (44.32 KiB) Viewed 7859 times
Re: Measure current ACS712 and ADS1115 are not working properly
The ADS1115 plugin is indeed a bit different from other plugins as it handles the complete measurement in a single call and thus you can have different tasks using the same chip only different ports.
That's probably not what you want as ADS1115A0#A0 gets updated, but you're also storing the last known value of ADS1115A1#A1 which is probably not yet updated when you call it here. (or it may be updated but not yet processed in the rules)
Code: Select all
On ADS1115A0#A0 do
let,1,[ADS1115A0#A0]
let,2,[ADS1115A1#A1]
let,3,[VAR#1]-[VAR#2]
TaskValueSet,8,1,[VAR#2]
TaskValueSet,8,2,[VAR#1]-[VAR#2]
endon
Re: Measure current ACS712 and ADS1115 are not working properly
About correcting the value, you can do it in the rules too.
Looks strange that the formula does not work, but when using the let command in the rules you can also perform calculations.
About the rules you posted...
Why not use [var#3] in the TaskValueSet? Simple calculations should work there, but better to do the calculations in a "let" command and use the variable when actually using the computed value.
Looks strange that the formula does not work, but when using the let command in the rules you can also perform calculations.
About the rules you posted...
Code: Select all
let,3,[VAR#1]-[VAR#2]
TaskValueSet,8,2,[VAR#1]-[VAR#2]
Re: Measure current ACS712 and ADS1115 are not working properly
Hi TD-er,
I have rewritten the rules and worked, thanks for the feedback.
Can you also help me how I calculate the current now?
A voltage divider for half the reference voltage (2.5 V) was installed on the A1. What does the formula look like in the form field?
I have rewritten the rules and worked, thanks for the feedback.
Can you also help me how I calculate the current now?
A voltage divider for half the reference voltage (2.5 V) was installed on the A1. What does the formula look like in the form field?
Code: Select all
on ADS1115A0#A0 do
TaskValueSet,8,1,[ADS1115A0#A0]
let,1,[ADS1115A0#A0]
EndOn
on ADS1115A1#A1 do
TaskValueSet,8,2,[ADS1115A1#A1]
let,2,[ADS1115A1#A1]
Let,3,[VAR#1]-[VAR#2]
TaskValueSet,8,3,[VAR#3]
EndOn
Re: Measure current ACS712 and ADS1115 are not working properly
Not sure how often voltage or current changes on your setup.
If it doesn't, then you don't need to tweak it, but if it does, you may want to make sure both tasks are executed as fast as possible after each other.
You could set a loop timer and call taskrun when handling the loop timer and then keep the rest of the rules as you have now, you can be sure both tasks are run at almost the same moment.
Just make sure the Interval set per task is set to a larger interval than your loop timer.
About the computation of a current.
Just to be clear, you are measuring the voltage over a shunt resistor?
If so, then the current is linear to the measured voltage: U = I x R => I = U / R
If it isn't as simple, please draw a schematic of how it is all setup.
If it doesn't, then you don't need to tweak it, but if it does, you may want to make sure both tasks are executed as fast as possible after each other.
You could set a loop timer and call taskrun when handling the loop timer and then keep the rest of the rules as you have now, you can be sure both tasks are run at almost the same moment.
Just make sure the Interval set per task is set to a larger interval than your loop timer.
About the computation of a current.
Just to be clear, you are measuring the voltage over a shunt resistor?
If so, then the current is linear to the measured voltage: U = I x R => I = U / R
If it isn't as simple, please draw a schematic of how it is all setup.
Re: Measure current ACS712 and ADS1115 are not working properly
... thanks for the hint, currently only the supply voltage is required and it is quite constant. Later I want to monitor other consumers. Then I can use loop timer well.Not sure how often voltage or current changes on your setup.
If it doesn't, then you don't need to tweak it, but if it does, you may want to make sure both tasks are executed as fast as possible after each other.
You could set a loop timer and call taskrun when handling the loop timer and then keep the rest of the rules as you have now, you can be sure both tasks are run at almost the same moment.
Just make sure the Interval set per task is set to a larger interval than your loop timer.
I managed to measure the current, thanks. When it comes to averaging, I'm still thinking about how I can do it.About the computation of a current.
Just to be clear, you are measuring the voltage over a shunt resistor?
If so, then the current is linear to the measured voltage: U = I x R => I = U / R
The transfer to the dummy task will be removed later, for control purposes only.
The rules now look like this, cumbersome but legible for me.
Code: Select all
on ADS1115A0#A0 do
TaskRun,10 // Spannungsteiler 0,5 x Busspannung [Bit]
TaskRun,12 // Busspannung [Bit]
let,1,[ADS1115A0#A0] // ACS7112 Spannung Out [Bit]
let,2,[ADS1115A1#A1]
let,3,[ADS1115A2#A2]
let,4,[VAR#3]*0.1875/1000 // Busspannung [Volt]
let,5,([VAR#3]-[VAR#2])*0.1875/1000 // Differenz Busspannung - 0,5 x Busspannung [Volt]
let,6,([VAR#1]-[VAR#2])*0.1875/1000 // ACS7112 Spannung Out [Volt]
let,7,[VAR#6]/0.185 // ACS7112 Curent Out [Amper]
let,8,[VAR#1]*0.1875/1000
TaskValueSet,8,1,[VAR#1]
TaskValueSet,8,2,[VAR#2]
TaskValueSet,8,3,[VAR#8] // Sensor Spannung
TaskValueSet,8,4,[VAR#4]
TaskValueSet,7,1,[VAR#4]
TaskValueSet,7,2,[VAR#5]
TaskValueSet,7,3,[VAR#6]
TaskValueSet,7,4,[VAR#7]
EndOn
Re: Measure current ACS712 and ADS1115 are not working properly
One example to perform filtering in rules: https://espeasy.readthedocs.io/en/lates ... ng-filters
Another really simple filter is to take the difference between old and new value and only apply a fraction of that difference to the old value.
In pseudo code:
diff = new - curval
curval = curval + (diff / 4)
This is an example of an IIR filter.
It will filter out spikes and changes will be more gradual.
However it will add an delay to the response (as does every filter).
So you may want to play around with the factor (1/4 in the example).
Making the factor lower (e.g. 1/8) will increase the delay and suppress fluke values even more.
Another really simple filter is to take the difference between old and new value and only apply a fraction of that difference to the old value.
In pseudo code:
diff = new - curval
curval = curval + (diff / 4)
This is an example of an IIR filter.
It will filter out spikes and changes will be more gradual.
However it will add an delay to the response (as does every filter).
So you may want to play around with the factor (1/4 in the example).
Making the factor lower (e.g. 1/8) will increase the delay and suppress fluke values even more.
Re: Measure current ACS712 and ADS1115 are not working properly
Hi TD-er,One example to perform filtering in rules: https://espeasy.readthedocs.io/en/lates ... ng-filters
I tried to calculate the mean of [VAR # 3] over 10 values.
But how, I tried it via an event, e.g. like this:
Code: Select all
on ADS1115A1#DiffA0A1ASC712 do
TaskRun,1
let,1,[ADS1115A0#SpannungsteilerA0]
let,2,[ADS1115A1#DiffA0A1ASC712]
let,3,([VAR#2]-[VAR#1])*0.1875/1000/0.1 // 0.1 für 20A Modul
event,Mittelwert=[VAR#3]
TaskValueSet,12,1,[VAR#1]
TaskValueSet,12,2,[VAR#2]
TaskValueSet,12,3,[VAR#3]
//TaskValueSet,12,4,[VAR#4]
EndOn
on Mittelwert do
Let,10,[VAR#9]
Let,9,[VAR#8]
Let,8,[VAR#7]
Let,7,[VAR#6]
Let,6,[VAR#5]
Let,5,[VAR#4]
Let,4,[VAR#3]
Let,3,[VAR#2]
Let,2,[VAR#1]
Let,1,[%eventvalue%]
TaskValueSet,12,4,([VAR#1]+[VAR#2]+[VAR#3]+[VAR#4]+[VAR#5]+[VAR#6]+[VAR#7]+[VAR#8]+[VAR#9]+[VAR#10])/10
EndOn
Re: Measure current ACS712 and ADS1115 are not working properly
You do set the same variables (1, 2 and 3) when receiving a value as you're using in the event Mittelwert.
So I guess you may want to use variables with a higher number in the Mittelwert event.
So I guess you may want to use variables with a higher number in the Mittelwert event.
Code: Select all
on Mittelwert do
Let,20,[VAR#19]
Let,19,[VAR#18]
Let,18,[VAR#17]
Let,17,[VAR#16]
Let,16,[VAR#15]
Let,15,[VAR#14]
Let,14,[VAR#13]
Let,13,[VAR#12]
Let,12,[VAR#11]
Let,11,[%eventvalue%]
TaskValueSet,12,4,([VAR#11]+[VAR#12]+[VAR#13]+[VAR#14]+[VAR#15]+[VAR#16]+[VAR#17]+[VAR#18]+[VAR#19]+[VAR#20])/10